spinksy13 
Member - Posts: 2
Member spacespace
Joined: May 28, 2017
Location: United Kingdom
Posted: May 28, 2017 at 12:44 AM / IP Logged Link to Post Post Reply Quote spinksy13
Hello,
We have a Hyundai 6000SE generator powering a 2.5kW borehole pump on our allotment site. When water is required the process is to start the generator via the ignition switch. The generator runs for one minute, to warm up, and then the pump kicks in. The generator manufacturer states that the pump should stop before the generator otherwise we could damage the AVR.
Can anyone suggest a circuit, probably using timer delay relays that allows the generator to run on for, say 30 secs, after the ignition switch is turned off?
The control system is 12Vdc and the pump is 240Vdc.
Regards
Spinksy13
tonanzith 
Gold - Posts: 593
Gold spaceThis member consistently provides reliable informationspace
Joined: July 18, 2008
Location: Washington, United States
Posted: June 25, 2017 at 1:10 AM / IP Logged Link to Post Post Reply Quote tonanzith
You want two standard relays.
One wires as follows:
Ground to pin 85
Positive trigger that runs your pump to pin 86
Constant 12v+ to pin 87a
And a wire from pin 30 that goes to pin 86 on another relay wired as the constant to momentary output relay at the following link:
https://www.the12volt.com/relays/page5.asp
Gary Sather
i am an idiot 
Platinum - Posts: 13,666
Platinum spaceThis member consistently provides reliable informationspace
Joined: September 21, 2006
Location: Louisiana, United States
Posted: June 25, 2017 at 12:01 PM / IP Logged Link to Post Post Reply Quote i am an idiot
https://www.the12volt.com/relays/page5.asp
Your link does not work. As drawn this only gives a half of a second. It is not going to be able to give 30 seconds.
tonanzith 
Gold - Posts: 593
Gold spaceThis member consistently provides reliable informationspace
Joined: July 18, 2008
Location: Washington, United States
Posted: June 25, 2017 at 9:50 PM / IP Logged Link to Post Post Reply Quote tonanzith
It says right in the diagram to adjust timed output to change the value of the capacitor. "Electrical engineer with 19 years in the industry AND an onan generator specialist". This setup will do what you want. Or you can purchase a timer module. I.e. A pac tr7......
Gary Sather
i am an idiot 
Platinum - Posts: 13,666
Platinum spaceThis member consistently provides reliable informationspace
Joined: September 21, 2006
Location: Louisiana, United States
Posted: June 26, 2017 at 2:38 PM / IP Logged Link to Post Post Reply Quote i am an idiot
Let me know what value capacitor he needs to achieve a 30 second delay. I guess what I meant to say was it is not going to be practical with just the capacitor. It will be much more practical for him to use a transistor and a capacitor. A much smaller value capacitor will work if used in conjunction with a transistor. Maybe you can draw that up for him.
tonanzith 
Gold - Posts: 593
Gold spaceThis member consistently provides reliable informationspace
Joined: July 18, 2008
Location: Washington, United States
Posted: June 26, 2017 at 11:26 PM / IP Logged Link to Post Post Reply Quote tonanzith
Firstly, my apologies. I did NOT see that the pump is 240v
My setup will work but not with a standard relay.
I would recommend a rib relay that will control both the 240v AC as well as the 12v DC.
A relay that can do this is the RIBH2C
It comes with a schematic ofngeneric wiring but for your needs you would hook commit from the pump to the rib white/yellow wire. And the hot wire to the pump goes to the rib white/brown wire. Then a constant 12v goes to the rib blue wire. And the rib yellow wire would go to pin 86 of a standard Bosch relay wired as the diagram in the link I sent you for constant to momentary output. Take the value of the capacitor in the diagram and multiply it appropriately for whatever time you desire. 15,30,45 seconds etc.
Gary Sather
spinksy13 
Member - Posts: 2
Member spacespace
Joined: May 28, 2017
Location: United Kingdom
Posted: June 27, 2017 at 3:22 PM / IP Logged Link to Post Post Reply Quote spinksy13
Hello,
Thanks for the feedback guys, much appreciated.
I'll look into the RIBH2C and see if I can source in UK.
Regards
Spinksy13

If you wish to post a reply to this topic, you must first login.
If you are not already registered, you must first register.

  Printable version Printable version Post ReplyPost New Topic
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot delete your posts in this forum
You cannot edit your posts in this forum
You cannot create polls in this forum
You cannot vote in polls in this forum

  •  
Search the12volt.com
Follow the12volt.com Follow the12volt.com on Facebook
Friday, March 29, 2024 • Copyright © 1999-2024 the12volt.com, All Rights Reserved Privacy Policy & Use of Cookies
Disclaimer: *All information on this site ( the12volt.com ) is provided "as is" without any warranty of any kind, either expressed or implied, including but not limited to fitness for a particular use. Any user assumes the entire risk as to the accuracy and use of this information. Please verify all wire colors and diagrams before applying any information.

Secured by Sectigo
the12volt.com spacer
the12volt.com spacer
the12volt.com spacer
Support the12volt.com
Top
the12volt.com spacer
the12volt.com spacer