hi 12 volt-ers,

my friend heats his home with an outdoor wood furnace that heats water and circulates it into the house thru baseboards. the pump on the little outdoor shed that houses the furnace that pumps the water has these specs:

"cartridge circulator"
1/8 horsepower
1.4 amps
60hz
115 volts
rpm 3250
max h2o temp 110 celcius or 230 farenheit

does anyone know of any 12v pumps that would work for this application? or how big a solar system with inverter would be needed if he keeps the original pump? thoughts on the best way to get his pump off the AC grid would be appreciated.

thanks,
jeremiah



Replies:

Posted By: lspker
Date Posted: January 30, 2011 at 9:51 PM
Most places that specilize in solar heating or green energy have dc pumps, you need to know the flow rate ghp  gallons per hour of pump




Posted By: oldspark
Date Posted: January 31, 2011 at 5:34 AM
A 300W inverter should handle it (115V x 1.4A = 161VA => 320VA (300W) using motor doubling rule).
If the motor does not handle modified-sine (= 2-level "stepped square wave", then a true-sine inverter is required.

Solar calcs need local data.
Assume 24 hour operation for 200W (assume inverter input is 200W) means AT LEAST 400W of panels, probably more like 600-800W depending.... (now only $3/W - so $1,200 - $2,400W of panels.
Battery - 12V system? (24V or 48V is better...)
Assume 24 hours reserve (no sun) => 200W x 24 = 48000W/12 = 4000AH over 24 hours = 167AH - say 12V 150AH to 160AH @ C20.
[In that scenario, I'd use two 12V 100AH deep cycle with 790 CCA wet-cell monoblocks (batteries) that sell here for about $220 each (compared to RRP $550 for a 75AH Optima blue top). Hence 200AH capacity and able to perform maintenance on one monoblock....


But for solar, I'd get a dc pump (d'oh!).
Why lose >20% by using an inverter?
And add the extra cost and unreliability?
And aren't dc motors more efficient?