I am trying to figure out how to use a relay in an power systems application for emergency power
down. 
 
Lets say that I have a 120V 20 A load.  I take a emergeny switch and connect it to a SPST relay so that when I hit this switch(lets say it is a normallyl open switch) it caused the load to loose power.  See if the magnetic coil is getting power and it needs it to keep the switch closed it would seem to me that you cannot use a NO emergency switch unless maybe you use a relay that is NC and then when I hit my switch it caused the loop to the magnetic coil to enegize forcing the switch open but then I have lost all DC power when was generating the DC power that most coils need in a relay.  Any input is welcomed.
 
Marcus
Mhouse
KarTuneMan 
Platinum - Posts: 7,056
Platinum spaceThis member has made a donation to the12volt.com. Click here for more info.spaceThis member consistently provides reliable informationspace
Joined: December 14, 2004
Location: Isle Of Man
Posted: February 14, 2005 at 6:33 PM / IP Logged  
Uhmm......ya....that sounds....uhm, good Industrial Application -- posted image.
overworked 
Copper - Posts: 133
Copper spacespace
Joined: November 09, 2004
Location: Australia
Posted: February 16, 2005 at 12:17 AM / IP Logged  
um......wanna try agin for us?....cant input what we dont understand
shoelesscraig 
Member - Posts: 43
Member spacespace
Joined: August 16, 2004
Posted: February 18, 2005 at 11:44 PM / IP Logged  
Didn't catch a word of that
flynntech 
Copper - Posts: 275
Copper spacespace
Joined: April 15, 2004
Location: United States
Posted: February 20, 2005 at 4:13 PM / IP Logged  
call an electrician.
the1alchemist 
Copper - Posts: 65
Copper spaceThis member has made a donation to the12volt.com. Click here for more info.spacespace
Joined: February 04, 2004
Location: United States
Posted: February 21, 2005 at 8:40 AM / IP Logged  
I THINK I got SOME of it...
First of all,there are relays with 120v coils,
assuming you have found one,I would suggest a normally open switch,just like in the car,you wouldn't want a relay energized all the time..
another prerequisite of the relay would be,to have a contact rating above your load(or at least the constant load rating equal to,and an inrush rating at least double(depending on capacitance issues with the load,like a huge motor,whatever,they should rate the equipment on a plaque somewhere))
just put the relay's com-NC in series with the current(assuming 120v,not 220..a 220 motor would need 2 relays if it is grounded)
then put your coil in series with your normally open switch,so....
when you hit the switch,the com/NC is now com-NO..no current flows...
as the others on the forum have already made clear,your request was very cryptic..so I hope this helps..there is always a solution...
'Stereo' Mike
The Audio CARtist,LLC
9600 Balt. Ave.
College Park,MD 20740
301-474-6260
mhouse 
Member - Posts: 2
Member spacespace
Joined: February 14, 2005
Location: United States
Posted: February 22, 2005 at 8:09 AM / IP Logged  
This was helpful.  Thanks.Industrial Application -- posted image.
Mhouse

Sorry, you can NOT post a reply.
This topic is closed.

  Printable version Printable version Post ReplyPost New Topic
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot delete your posts in this forum
You cannot edit your posts in this forum
You cannot create polls in this forum
You cannot vote in polls in this forum

  •  
Search the12volt.com
Follow the12volt.com Follow the12volt.com on Facebook
Sunday, April 28, 2024 • Copyright © 1999-2024 the12volt.com, All Rights Reserved Privacy Policy & Use of Cookies
Disclaimer: *All information on this site ( the12volt.com ) is provided "as is" without any warranty of any kind, either expressed or implied, including but not limited to fitness for a particular use. Any user assumes the entire risk as to the accuracy and use of this information. Please verify all wire colors and diagrams before applying any information.

Secured by Sectigo
the12volt.com spacer
the12volt.com spacer
the12volt.com spacer
Support the12volt.com
Top
the12volt.com spacer
the12volt.com spacer