Ok... thanks again everyone for helping explain.For a while there it seemed to be bordering on the absurd..which Is why I mentioned the pet choking thing..a little sarcarsm to lighten things up.
Anyhow...some things I may also need help with on the subject. Were discussing situations in which voltage fluctuates constantly..such as in a vehicle. I would assume some kind of voltage regulation is used in any 12v automotive amplifer to help compensate..for normal as well has more extreme fluctuations.
But regardless......dealing with this specific post..and my original reply...lets take this example.
Ok..a 400w amp....and a 15ft run of power wire. For the sake of this dicussion I will leave out fusing and other obvious issues..I just want to deal with wire gauge and what I belive the effects should be.
I used math..ohms law and a current draw calulator.I came to these conclusions...
using ohms law@ 12v the maximum current draw should beroughly 33.3a. At 14.4....roughly 27.7. So I averaged the current draw to be 30a @ 400w.
using a 4ga wire..(resistance of .25m ohm per foot) a run of 15 feet will have a Vdrop of approx. .11v.
An 8ga. (.63m ohm per foot) @ 15 feet = Vdrop of approx .28v.
A 10ga. (a little under 1ohm for a 15 ft run) should have a Vdrop of approx .44v..less then 1/2 a volt.
And these calculations are maximum assuming max draw at all times.
So I guess where I am going with this is does anyone really belive the difference in voltage drop using the 10ga is really enough to burn stuff up?? The normal voltage fluctuations in a vehicle far exceed the difference in Vdrop caused by the wire gauge...and remember..I am talking about the question from the OP..not hypotheticals or sytems running at 1ohm..or massive current draw that exceeds the limits of conventional charging systems etc.
Now before anyone jumps on me..lol...PLEASE realize I am not trying to arugue that it is ok to use a smaller wire ga. then required..I never do that..as a matter of fact I am notorious for overkill when it comes to audio system wire size...but it is the reason why I use the larger wire we seem to have some differnet opinion about..well at least in the case with this 400w amp.
Where I do have some issue...is believing that in this particular post ..that the extra heat caused by using a 10 ga wire would be substantial enough to cause concern...or should there be concern..but perhaps about as much as a pet choking on a speaker wire..lol sorry had to add that. I do plan on doing some experiments with wire gauge and amp temp in the future..I want to find out how much difference it make as far as heat being a major concern. I won't bother with anything ridiclous like running a 1000w amp off an 18ga..although it would be fun watching the wire insulation burn off..but something similar to this situation where using "border line" wire ga. vs. whats called for vs. overkill.
Thanks again guys..great stuff.