Do you want a chance to rewrite that before I answer?
Ooops - too late!
A fuse rated "
less than the actual load?"...
No - because then the fuse would constantly blow wouldn't it? (Ha ha, I finally get the chance to get sarcastic and dig the knife way in....
) [ BTW - I rarely go to the trouble to include emoticons. To do so would require the utmost care and concern by me.... ]
The "Rules":
A fuse must be rated to handle the load - ie, at least equal to the load.
Usually that is the max expected load - eg, at max volume, or max current (light output) at highest voltage - but you might decide lower is ok (eg, 5A for a 10A amp where you don't expect to go higher than ~1/4 max volume or half full output) - not that you can do that with lights.
And there is a general fusing/protection/wiring design rule - namely that fuses (and wires & relays etc) should not normally run at higher than ~70% of its rating, though sometimes 90% may be designed (and sometimes 110% in
reality - noting that a fuse or breaker may last indefinitely on a 110% loading (10% overload)).
Hence for a 50W HID, IMO...
Assuming 50W HID means output hence ~60W input...
Or using the usual ROT (rule of thumb) - divide the power by 10 to get current - hence 50W/10 = 5A.
[ FYI - The 10 is simple, and it tends to factor in the "conversion" from output to input (at say 80% efficiency) or that 12V really means up to 14.4V etc and that rating may be based on old 13.8V car voltages if not newer 14.2 or 14.4V, or even 12.0V.
]
So 5A. That fits in well with st'd fuse sizes (unlike 4A), but then if we apply the 70% rule it means a 7.5A or 10A fuse.
But now the important thing -
WHAT are we fusing? (Or rather, WHAT are we protecting?)
It might be to protect the source - ie, battery or alternator - but that's not relevant here. (Let's assume some "master" upstream fuse or flink (fuselink) does that.)
Usually it's to protect the load. And that's where people get con-fused. (Ah yes, a Master of Punnery.]
The "load" is anything downstream from the fuse, and in our cases they are rarely for equipment protection - ie, HUs, amps, CPUs etc have their own fuses specifically designed to protect that equipment.
Hence our protection/fusing is almost always for the
distribution - ie, wires, connectors, relays.
And the fuse rating (Amps) must not exceed the smallest rating downstream - ie, a 10A cable can have a 10A or 7.5A or 5A or 250mA fuse but NOT a 15A or 30A or 200A fuse.
Note however that a fuse only protects its
distribution until the next fuse. I'll call that segmentation...
So, your design...
You know you need (say) 5A for each 50W HID. Hence you need cable rated for (at least) 5A.
You might use 5A cable and hence a 5A fuse. I'd probably use a 10A or larger cable but could then use a 5A or 7.5A or 10A fuse (anything up to the cable rating).
Remember - that fuse is to prevent the wire from flaming if it shorts to GND. The fuse must blow before the cable has a chance to get too hot...
And why use larger than necessary cables? To minimise the voltage drop. Or because it's what I happen to have on hand and isn't too expensive or big or heavy...
Now, not that I know your design (hey man, emoticons are one thing, but to actually read what has previously been written in a thread... c'mon, get real!!), but...
Two "5A HIDs" (ie, each with their 5A fuse & cable or 10A fuse & 15A cable etc) could be joined to a 10A distribution which might be a 10A fuse & 10A cable, or 15A or 20A fuse with a 20A cable etc.
Likewise all loads can be joined.
One danger you have is the splitting of the main feeder's core. Since they are not individually fused (upstream), if any were to short to GND
or if an individual load exceeded that split's actual current carrying capacity...
An outright short is probably not an issue since its current should be many times the upstream fuse rating, but it is any overload less than a direct short that is the danger.
Provided a split's downstream fuse is rated
reasonably below the split's capability, it may not be a big issue. IE 8G. Assume a 60A rating. 4 splits in theory about 15A each (not that that logic always follows!). But you would
not use a 15A downstream fuse... 10A maybe. The splits may be uneven, hence 13A or 12A etc. But also we do want the fuse to blow before the cable melts in an
overload situation (ie, not a direct short). And since a fuse takes
s time to blow at
x overload and a cable takes
t time to blow at the same
x overload, we want to ensure the fuse time
s is less than cable time
t, hence in simple terms that the fuse is
reasonably smaller than the presumed split rating.
Simple eh? Of course most would say that such splits are unacceptable for the reasons I outlined and hence a DB (distribution block) or similar
must be used - and professionals may have no choice on the matter - but I try to point out that "protection" can be physical instead of (or as well as) electrical, and there are different protection modes (overload, shorts, equipment protection).
And I've seen enough installations that follow the rules that are IMO outright dangerous - eg, battery safety isolation switches on the +12V side, or useless and dangerous alternator-battery fuses as per
big 3 upgrade on integra fuse box?. Even oft quoted rules like fusing within
x mm/inches are not really rules at all - I prefer
'as close as practicable' to the battery (noting that
practicable is the key word and subject to expert and legal opinion...).
But I have written much on the above issues before - as well as on using self resetting circuit breakers for critical lights (and probably having them on separate distributions) - and I've repeated way too much here.
As to your 10A for twin 55W HQs, you'll have figured that's probably a bit low (but see comments re my 10A CBs below).
Though 55W HQs are 55W input, the 'div by 10' rule is till good as it factors in distribution NOT running at 100% of rating (tho the div-10 rule tends to assume EITHER an 80% efficiency ELSE a vehicle's voltage variation, whereas fuses etc might normally be consider a 70% loaded device).
Hence 2 x 55W = 110W => 110/10 => 11A, hence a 15A fuse and cable. 10A may be ok, but why cut so close?
Likewise the 120W LED => 12A => 15A distribution.
Hey - does that work out nicely? All cabling from the feeder could be 15A (or higher) rated cable with 15A fuses.
Of course that depends on how the 8G is rated and hence what each split can carry. (Different people use different cable current rating methods & tables. I never use them since I work from what I consider an acceptable overall voltage drop and that is always less than what
the industry considers acceptable.)
BTW - it doesn't matter if the total of the downstream (split) fuses exceed the feeder cable rating since the feeder's fuse (60A?) will protect that cable. Of course if that blows. you lose all.
[ FYI - hence my car's main beam distribution via
huge flinks intended never to blow (2 of; I can't recall if they are 50A or 60A or 100A; nor if I split as hi/low or left/right, tho probably the latter) which then feed relays each with self resetting circuit breakers. Though at the moment I'm using 3 relays for 6 filaments (4 lights), I intend to revert to my traditional dedicated relay per filament. The breakers are rated at 30A (for 2 100W inner highbeams) and 10A for the others that feed 65/55W H4s (normally they'd be 15A breakers assuming 100/90W or 100/55W H4s, but I have not had problems with
mere 10A breakers (fuses) on what is obviously at least a 2x55W load (probably 55+65 = 120W or maybe even 65+65 = 130W). But I recall replacing the original 15A CBs with 10A CircuitBreakers to see what would happen...
]
Anyhow, that's my design theory along with actual observations.
BTW - my cabling well exceeds load requirements and fuse/breaker ratings. It met my design of
no more than 0.5V less [across the bulbs compared to the source (ie battery or alternator output).
Always nice writing a quickie before a sat'dy night gig.
PS - I started writing this before your last reply. I wonder why I took so long to write?